Free 186 More Best Homemade Tools eBook:  
Get 2,000+ tool plans, full site access, and more.

User Tag List

Page 11 of 23 FirstFirst 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 LastLast
Results 101 to 110 of 227

Thread: Rotary Phase Converter (Create 3-phase power from a single phase source)

  1. #101
    Supporting Member Frank S's Avatar
    Join Date
    Aug 2015
    Location
    Peacock TX
    Posts
    11,212
    Thanks
    1,983
    Thanked 8,786 Times in 4,206 Posts

    Frank S's Tools
    They are downloading now but I should have waited until I had a lower internet usage going on LOL

    186 More Best Homemade Tools eBook
    Never try to tell me it can't be done
    When I have to paint I use KBS products

  2. #102
    Supporting Member smithdoor's Avatar
    Join Date
    Feb 2016
    Location
    Clovis CA
    Posts
    59
    Thanks
    0
    Thanked 16 Times in 9 Posts
    This is three-phase to two-phase transform
    I have only seen this in books and was uses around 1900
    I was told by a old electrician is use for 115 volts for offices and last time he ever saw was in build built in the 1920's

    Dave
    Attached Thumbnails Attached Thumbnails Rotary Phase Converter (Create 3-phase power from a single phase source)-screenshot-1-.jpg  

    2000 Tool Plans

  3. #103
    Supporting Member nhengineer's Avatar
    Join Date
    Aug 2016
    Posts
    187
    Thanks
    10
    Thanked 65 Times in 37 Posts

    nhengineer's Tools
    Quote Originally Posted by old kodger View Post
    Rhengieer,
    I thank you for your effort, but now you see what I mean when I say, in Australia most of the options to date are totally uneconomic, for instance, I need to power a 3 phase mig welder which is name-plated at 10 amps per phase which is about 7.1kw at 230 volts. If a 3hp transformer is likely to cost $450 US that's around $600 AU, and I might need two...$1200 plus freight, and as I mentioned before freight from the US to AU needs the surrender of ones first born, I would not be surprised to find that the freight exceeded the initial cost of the transformers. Also 3hp would woefully inadequate, I need at least 10 amps per phase, for a overload margin, maybe more.
    So at a potential cost in excess of $2400, a second hand 3 phase generator is starting to look a lot more realistic.
    I thank you for all your effort, and indeed to all the other contributors to this thread, but unless I can find a way to control a synchronous motor acting as a generator, I have two options:- buy a generator or attempt to rewire the welder to run on single phase. Incidentally, I'm informed by the manufacturers of the welder, that the configuration internally is actually three separate transformers feeding a bank of full wave bridges, so it could be possible.
    If anyone is interested I'll keep you informed.

    Rob.
    Rob,

    Are there no transformer manufacturers in Australia?

    David Lee
    (NHEngineer)

  4. #104
    Supporting Member nhengineer's Avatar
    Join Date
    Aug 2016
    Posts
    187
    Thanks
    10
    Thanked 65 Times in 37 Posts

    nhengineer's Tools
    Quote Originally Posted by smithdoor View Post
    This is three-phase to two-phase transform
    I have only seen this in books and was uses around 1900
    I was told by a old electrician is use for 115 volts for offices and last time he ever saw was in build built in the 1920's

    Dave
    Why would anyone want to go from 3-phase to 2-phase?

  5. #105
    Supporting Member nhengineer's Avatar
    Join Date
    Aug 2016
    Posts
    187
    Thanks
    10
    Thanked 65 Times in 37 Posts

    nhengineer's Tools
    Quote Originally Posted by smithdoor View Post
    How are using this transformer
    I was thinking this for single to three phase
    Most motors that are 415 volt can also be wire 240 they wye/delta wound motors
    I think take close look at the motor to see what type it is most wye delta motor are 6 wire type

    Dave
    I think I'll make a 2-phase DC alternator.

  6. #106
    Supporting Member Frank S's Avatar
    Join Date
    Aug 2015
    Location
    Peacock TX
    Posts
    11,212
    Thanks
    1,983
    Thanked 8,786 Times in 4,206 Posts

    Frank S's Tools
    Quote Originally Posted by nhengineer View Post
    Rob,

    Are there no transformer manufacturers in Australia?

    David Lee
    (NHEngineer)
    David I know of 2 or 3 guys who make their own transformers 1 lives on Flinders Island Au another over in NewZeeland Not sure wher the other guy lives but I have used his online calculator to make several small buck & boost and step down transformers. He goes by the username of Josetue the link to his spreadsheet is on his post on this page about halfway down
    From New SMA INVERTER SI6.OH-11, battery full 50HZ Jumps to 60Hz
    OZtules is a foremost authority on building power inverters and just about any other off grid power generation His 6KW pure sine inverters have been made by several. I'm not sure about their 3 ph activity though but their published information is well worth having a look at
    Here is a link to Joestue's spreadsheets
    Index of /bulk/spreadsheets
    I downloaded your RPC plans and had a look at them You used a different approach than what I have, but very informative and well written thanks When I build my next 8hp RPC I can see incorporating your plans with the way my current RPC is made because I like having the capacitors to balance out the ph shift
    Never try to tell me it can't be done
    When I have to paint I use KBS products

  7. #107
    Supporting Member smithdoor's Avatar
    Join Date
    Feb 2016
    Location
    Clovis CA
    Posts
    59
    Thanks
    0
    Thanked 16 Times in 9 Posts
    FYI
    I have made my own transform a long time ago. The hard part is find a core the low cost way was to build a TOROID type and use gal electric fence wire simple to wind into a dough shape. The in recent I used is microwave transform core

    In some parts of world they use a bank of capacitors for AC 3 phase when they only have single phase power. But only works when have the same load on the motor. This not work for machine tool or air compressor as the load changes.

    At one time in life look into or try ever way as shop only had single phase. I finally landed on four ways

    1) change the motor
    2) rotary converter
    3) static converter
    4) motor generator

    I did at time have over 20 employs working for me manufacturing aircraft hangar doors

    Dave





    Quote Originally Posted by Frank S View Post
    David I know of 2 or 3 guys who make their own transformers 1 lives on Flinders Island Au another over in NewZeeland Not sure wher the other guy lives but I have used his online calculator to make several small buck & boost and step down transformers. He goes by the username of Josetue the link to his spreadsheet is on his post on this page about halfway down
    From New SMA INVERTER SI6.OH-11, battery full 50HZ Jumps to 60Hz
    OZtules is a foremost authority on building power inverters and just about any other off grid power generation His 6KW pure sine inverters have been made by several. I'm not sure about their 3 ph activity though but their published information is well worth having a look at
    Here is a link to Joestue's spreadsheets
    Index of /bulk/spreadsheets
    I downloaded your RPC plans and had a look at them You used a different approach than what I have, but very informative and well written thanks When I build my next 8hp RPC I can see incorporating your plans with the way my current RPC is made because I like having the capacitors to balance out the ph shift
    Last edited by smithdoor; Jan 20, 2017 at 10:50 AM.

  8. #108
    Supporting Member nhengineer's Avatar
    Join Date
    Aug 2016
    Posts
    187
    Thanks
    10
    Thanked 65 Times in 37 Posts

    nhengineer's Tools
    Quote Originally Posted by Frank S View Post
    David I know of 2 or 3 guys who make their own transformers 1 lives on Flinders Island Au another over in NewZeeland Not sure wher the other guy lives but I have used his online calculator to make several small buck & boost and step down transformers. He goes by the username of Josetue the link to his spreadsheet is on his post on this page about halfway down
    From New SMA INVERTER SI6.OH-11, battery full 50HZ Jumps to 60Hz
    Do you mean you boys down there need to import things like this? Crikie! I could come down there, open up a shop and get rich!

    Quote Originally Posted by Frank S View Post
    OZtules is a foremost authority on building power inverters and just about any other off grid power generation His 6KW pure sine inverters have been made by several. I'm not sure about their 3 ph activity though but their published information is well worth having a look at. Here is a link to Joestue's spreadsheets
    Index of /bulk/spreadsheets
    You don't need a 3-phase transformer. Single phase boost transformer ANSI schematic below:

    Rotary Phase Converter (Create 3-phase power from a single phase source)-lcmagnetics230vacboosttransformer.jpg Sorry, I've not yet been able to finger out those ISO symbols.

    The output section is configured so that there is a 180° phase shift from one output to the other. That will give you two 230V outputs a half phase apart. That is what we have for residential high voltage here in the USA (except it's 240-250V). With that you can use that at the input to my design and create (kind of) a 230V 3-phase suitable to run your 230V, 3-phase motors with reduced horsepower output (83.3% of the nameplate rating)

    Quote Originally Posted by Frank S View Post
    I downloaded your RPC plans and had a look at them You used a different approach than what I have, but very informative and well written thanks When I build my next 8hp RPC I can see incorporating your plans with the way my current RPC is made because I like having the capacitors to balance out the ph shift
    Thank you for the compliment.
    Last edited by nhengineer; Jan 20, 2017 at 12:52 PM.

  9. #109
    Supporting Member
    Join Date
    Oct 2016
    Posts
    1,113
    Thanks
    25
    Thanked 345 Times in 242 Posts

    old kodger's Tools
    Rhengineer,
    You possibly could come down here and get rich,........provided you're prepared to import a shipping container full at a time, it's the freight that kills us. If I buy a Briggs and Stratton engine here, it'll cost me $100 per hp, I used to run a business mowing grass, and at the time a 20hp engine was $2000 plus gst (10%) when the US price for the same engine was $400 plus freight, but it still meant that I could land it here for around $1000.
    The answer to the question of do we have to import this stuff...yup! because the local cost is even greater.

    Rob.

  10. #110
    Supporting Member smithdoor's Avatar
    Join Date
    Feb 2016
    Location
    Clovis CA
    Posts
    59
    Thanks
    0
    Thanked 16 Times in 9 Posts
    FYI
    back 2002 for a shipping container 40' long [12.2 meters long] From the USA to part of work cost FOB dock $6,000.00 Plus $500.00 from my shop to the dock.

    Dave

    Quote Originally Posted by old kodger View Post
    Rhengineer,
    You possibly could come down here and get rich,........provided you're prepared to import a shipping container full at a time, it's the freight that kills us. If I buy a Briggs and Stratton engine here, it'll cost me $100 per hp, I used to run a business mowing grass, and at the time a 20hp engine was $2000 plus gst (10%) when the US price for the same engine was $400 plus freight, but it still meant that I could land it here for around $1000.
    The answer to the question of do we have to import this stuff...yup! because the local cost is even greater.

    Rob.

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments