Results 1 to 10 of 227
Thread: Rotary Phase Converter (Create 3-phase power from a single phase source)
    Not to be splitting hairs here but the term for the US 2 120V lines coming into a house is called split phase and yes it is actually created from center tapping the transformer on the pole to create the neutral. I one looks up on the crossbar of the pole and sees only 2 wires for the transmission lines 1 is the ground and the other is the 13.2 KV high voltage the 3 out put lugs will be 120-0-120 or communally known as L1 N L2 when this enters the service panel the N or common is connected to the terminal strip on the side of the panel this is where all of the white wires are connected the bare ground wires are also connected to this terminal strip or may be connected to a desperate terminal strip but even so both terminal strips are connected together to the incoming neutral Plus the wire coming from the grounding rod driven in the ground near the main panel creating what is called a bonded ground
    Now all 220v appliances receive their power from the L1 and the L2 and would be perfectly happy to have only 2 wires connected to them except for 2 things first would be the lack of safety without the ground . 2nd all controlling circuits are derived from either the L1+ the neutral/ground or the L2 + the neutral/ground in some rare instances where there happens to be more than 1 set of controlling circuits or the load of the controlling circuits and other 120v loads are enough to create an imbalance the loads may be split between both lines.
    European 230v single phase equipment have only 1 power leg and 1 neutral leg+ ground
    Now a 220v rotary phase converter in the US can actually be nothing more than a simple 3Ph motor with the 2 120v lines connected to the T1 and T1 terminals of the motor but this will not allow it to start up because as mentioned in previous posts the legs are actually 180° apart. Therefore some means to starting it to rotate is required this is accomplished by using either a pony motor to spin it up or a bank of capacitors connected to to the L1 or L2 at the T1 or T2 terminal and the neutral line to charge the capacitors the output terminal of the capacitors is connected to the T3 terminal. It is best to have a switch or a timed relay to charge the capacitors before switching on the converter motor but in the case of my 2 HP converter there is none this means the converter can take up to 15 seconds before reaching run Speed. on larger converters this would mean the inrush current would remain high for several seconds and possibly even a full minute which could cause a breaker to trip.
    There was a discussion about single phase capacitor start single phase 220v motors in these there is a separate winding that is wound 1 tooth out of sync with the other winding's there is also a centrifugal switch that cuts the start winding from circuit after the motor reaches full speed. There are also motors with both start and run capacitors this is to assist in balancing the loads of the field winding's' when the motor is under load this arrangement is usually found in single phase motors that are started and ran constantly under heavy loads.
    Some larger 3 phase motors are wired both in star and delta with 2 magnetic motor controllers these will be started with star then once up to speed will switch to delta or vice versa I forget which.
    Then there is the DC start motors which are usually in the size range of or 1200 HP or more where the motor uses very high amperage 96 VDC to make it start rotating then as the RPMs increase it is switched to 4100 or 4300 Volts AC
    1 last note if there are 3 wires on the pole it means that there are 2 13.2 KV lines and 1 ground all is needed there would be a 2nd transformer to get 3 ph by using the center tap method of the first and tying 1 leg to 1 of the input legs of the other then another connection is made from the grounds and one other lug I forget which it is but the output will be 120 198 120 which will give about 208 across any 2 legs
    for true 220/240v 3 phase or 460V this requires there to be 4 wires on the pole and 3 transformers for the incoming line voltage
    I hope I have not completely confused the issue
    that_other_guy (Dec 10, 2018)
