That looks like a mechanically strong joint since the center wire is bend over after the two wires are wrapped around it. However it is not a good electrical connection, unless it is soldered. There is some level of "spring back" with any metal being bent, even soft copper. The two outer wires are not really tight against the center wire. You would be able to easily slide that center wire out if it was not bent over. It will pass current, but the connection is loose, the conductors are not in intimate contact with each other. That will be a point of high resistance in the circuit. It will create heat in use. Heat creates corrosion, corrosion creates resistance, resistant creates more heat. That connection will eventually fail if it is used at or near maximum current for that size conductor.
A couple of times I have been called to replace a circuit breaker that seems to trip on its own. When reset, it will work fine for a while. Both of these were during a holiday when the kitchen range was in use, all 4 surface elements and the oven in use at the same time. Pulling maximum current for the circuit. BUT not enough to trip the breaker. On inspection, the wire connections to the breaker were loose. This created heat at the breaker connection. The external heat caused the breaker to trip, not heat from over current.