    Yes they change the voltage starting 1980's was switching from 240 to 230 volts it was a 20 year plan with a low limit of 216 to high limit of 253 volts. This at the meter
    If you have long run from the meter to tool you then have a greater drop
    So if need to adjust for a motor it simple with a buck and boost

    As far as 50 Hz to 60 Hz
    The tools I had it past that had 50Hz motor I just ran tools for 20 year or more on 60Hz be for selling the tools working great on 60Hz. Some castes I replace the pulley with smaller one so RPM plate was right.

    Dave

  2. #2
    Supporting Member Frank S's Avatar
    Join Date
    Aug 2015
    Location
    Peacock TX
    Posts
    12,615
    Thanks
    2,677
    Thanked 11,103 Times in 5,386 Posts

    Frank S's Tools
    My rotary phase converter is kind of small actually too small in some ways,being only a 3 Hp it is started by the use of 3 large capacitors with no small spin up motor. I really need to build a larger one with a spin up motor but it came with my lathe when I bought it and has been running it for a few years even though my lathe is 4 hp, as long as I don't try to make a .200" cut @ .015" feed it does just fine any heavier cut and it will bog down.Also I have found that if I switch on my 3 Hp mill and just allow the motor to run without any work being done then the lathe do a little better when starting it or reversing it.
    I an thinking that when I build a larger converter I will use a 1/2 or 3/4 Hp spin up motor direct coupled to a 7.5 or 10 Hp motor with a large flywheel to help with the higher current load my 450 Amp mig welder will require
    Last edited by Frank S; Jan 6, 2017 at 11:56 AM.
    Never try to tell me it can't be done
    When I have to paint I use KBS products

  3. #3
    Supporting Member smithdoor's Avatar
    Join Date
    Feb 2016
    Location
    Clovis CA
    Posts
    59
    Thanks
    0
    Thanked 16 Times in 9 Posts
    They not hard to build
    I have simple drawing just using a AC potential relay and starting capacitor

    Here is the drawing

    Dave

    Quote Originally Posted by Frank S View Post
    My rotary phase converter is kind of small actually too small in some ways,being only a 3 Hp it is started by the use of 3 large capacitors with no small spin up motor. I really need to build a larger one with a spin up motor but it came with my lathe when I bought it and has been running it for a few years even though my lathe is 4 hp, as long as I don't try to make a .200" cut @ .015" feed it does just fine any heavier cut and it will bog down.Also I have found that if I switch on my 3 Hp mill and just allow the motor to run without any work being done then the lathe do a little better when starting it or reversing it.
    I an thinking that when I build a larger converter I will use a 1/2 or 3/4 Hp spin up motor direct coupled to a 7.5 or 10 Hp motor with a large flywheel to help with the higher current load my 450 Amp mig welder will require
    Attached Thumbnails Attached Thumbnails Rotary Phase Converter (Create 3-phase power from a single phase source)-three-phase.jpg  

  4. #4
    Supporting Member
    Join Date
    Oct 2016
    Posts
    1,113
    Thanks
    25
    Thanked 423 Times in 296 Posts

    old kodger's Tools
    Hi Paul,
    I had been thinking about a 230-0-230 volt transformer arrangement such as is used in electronic circuit supplies (usually 25-0-25 for medium output amplifiers), however, as you point out, the phases are in fact 180 degrees out of phase not 120 and I did wonder how that would effect the performance of the motor, in that it would "confuse" the third phase orientation.

    Regards,

    Rob.

  5. #5
    Supporting Member Paul Alciatore's Avatar
    Join Date
    Mar 2014
    Location
    Beaumont, TX
    Posts
    304
    Thanks
    9
    Thanked 200 Times in 110 Posts

    Paul Alciatore's Tools
    Rob,

    I feel your doubt. In fact, in spite of a background in physics and math, it took me some time to come to the realization that it is possible to get real three phase from a pair of Voltages that are 180 degrees out of phase with each other. It seems to be contradictory, I mean just how do two Voltages that are 180 degrees out of phase suddenly become 120 degrees out of phase? In most phase converters those original two phases are just passed through with no change. But when you do the vector math, it really does work. In fact, this is exactly what is happening when, here in the US, we take a 220V feed (call it single phase or two phase as you like, that's just terminology) and, using a rotary phase converter to convert it to three phase.

    The "magic" lies in the vector math which shows a change in the ground reference. When a rotary phase converter is used to generate a third leg from the two existing phases of the power feed, although it does not actually generate an actual, new ground point, the third phase is generated in a manner so that the theoretical ground point is shifted in both Voltage and phase from the original ground point that is half way between the original two phases. And those original two phases are not changed in any way, but from the viewpoint of this new, theoretical ground point they REALLY are 120 degrees out of phase. This is at the same time that those original two legs are still 180 degrees out of phase when viewed from or referenced to the original, earth ground point. It sounds contradictory and I had to work out all the math before I was ready to believe it, but it does really work.

    So, if you first convert the real single phase current which has one side grounded and the other at 220V to the 110V-G-110V configuration used in the US and then run it through a rotary phase converter, then you do get actual, true three phase. In fact, if you are using a rotary phase converter, you do not even have to use the transformers to convert it to 110V-G-110V, you can just use the 220V power from the wall outlet directly to the rotary phase converter and it will still work and produce true three phase.

    This will also work for any other kind of phase converter that produces three phase from single/two phase. I talked about using the transformers because I do not have a copy of the plans being sold and I do not know if they require the center ground of the 110V-G-110V system or not. There are many schemes for producing three phase from 110V-G-110V and some of them may very well need that center ground.



    Quote Originally Posted by old kodger View Post
    Hi Paul,
    I had been thinking about a 230-0-230 volt transformer arrangement such as is used in electronic circuit supplies (usually 25-0-25 for medium output amplifiers), however, as you point out, the phases are in fact 180 degrees out of phase not 120 and I did wonder how that would effect the performance of the motor, in that it would "confuse" the third phase orientation.

    Regards,

    Rob.

  6. #6
    Supporting Member Frank S's Avatar
    Join Date
    Aug 2015
    Location
    Peacock TX
    Posts
    12,615
    Thanks
    2,677
    Thanked 11,103 Times in 5,386 Posts

    Frank S's Tools
    Not to be splitting hairs here but the term for the US 2 120V lines coming into a house is called split phase and yes it is actually created from center tapping the transformer on the pole to create the neutral. I one looks up on the crossbar of the pole and sees only 2 wires for the transmission lines 1 is the ground and the other is the 13.2 KV high voltage the 3 out put lugs will be 120-0-120 or communally known as L1 N L2 when this enters the service panel the N or common is connected to the terminal strip on the side of the panel this is where all of the white wires are connected the bare ground wires are also connected to this terminal strip or may be connected to a desperate terminal strip but even so both terminal strips are connected together to the incoming neutral Plus the wire coming from the grounding rod driven in the ground near the main panel creating what is called a bonded ground
    Now all 220v appliances receive their power from the L1 and the L2 and would be perfectly happy to have only 2 wires connected to them except for 2 things first would be the lack of safety without the ground . 2nd all controlling circuits are derived from either the L1+ the neutral/ground or the L2 + the neutral/ground in some rare instances where there happens to be more than 1 set of controlling circuits or the load of the controlling circuits and other 120v loads are enough to create an imbalance the loads may be split between both lines.
    European 230v single phase equipment have only 1 power leg and 1 neutral leg+ ground
    Now a 220v rotary phase converter in the US can actually be nothing more than a simple 3Ph motor with the 2 120v lines connected to the T1 and T1 terminals of the motor but this will not allow it to start up because as mentioned in previous posts the legs are actually 180° apart. Therefore some means to starting it to rotate is required this is accomplished by using either a pony motor to spin it up or a bank of capacitors connected to to the L1 or L2 at the T1 or T2 terminal and the neutral line to charge the capacitors the output terminal of the capacitors is connected to the T3 terminal. It is best to have a switch or a timed relay to charge the capacitors before switching on the converter motor but in the case of my 2 HP converter there is none this means the converter can take up to 15 seconds before reaching run Speed. on larger converters this would mean the inrush current would remain high for several seconds and possibly even a full minute which could cause a breaker to trip.
    There was a discussion about single phase capacitor start single phase 220v motors in these there is a separate winding that is wound 1 tooth out of sync with the other winding's there is also a centrifugal switch that cuts the start winding from circuit after the motor reaches full speed. There are also motors with both start and run capacitors this is to assist in balancing the loads of the field winding's' when the motor is under load this arrangement is usually found in single phase motors that are started and ran constantly under heavy loads.
    Some larger 3 phase motors are wired both in star and delta with 2 magnetic motor controllers these will be started with star then once up to speed will switch to delta or vice versa I forget which.
    Then there is the DC start motors which are usually in the size range of or 1200 HP or more where the motor uses very high amperage 96 VDC to make it start rotating then as the RPMs increase it is switched to 4100 or 4300 Volts AC
    1 last note if there are 3 wires on the pole it means that there are 2 13.2 KV lines and 1 ground all is needed there would be a 2nd transformer to get 3 ph by using the center tap method of the first and tying 1 leg to 1 of the input legs of the other then another connection is made from the grounds and one other lug I forget which it is but the output will be 120 198 120 which will give about 208 across any 2 legs
    for true 220/240v 3 phase or 460V this requires there to be 4 wires on the pole and 3 transformers for the incoming line voltage
    I hope I have not completely confused the issue
    Never try to tell me it can't be done
    When I have to paint I use KBS products

  7. The Following User Says Thank You to Frank S For This Useful Post:

    that_other_guy (Dec 10, 2018)

  8. #7
    Supporting Member
    Join Date
    Oct 2016
    Posts
    1,113
    Thanks
    25
    Thanked 423 Times in 296 Posts

    old kodger's Tools
    Hi Dave,
    These are precisely the considerations that have stopped me proceeding with experiments in that area to date.
    I have seen commercial converters and I think that they use a lead and lag circuit based on inductors for one side and capacitors for the other leaving a primary circuit in the middle as the center phase, but they're very expensive.
    Regards,
    Rob.

  9. #8
    Supporting Member smithdoor's Avatar
    Join Date
    Feb 2016
    Location
    Clovis CA
    Posts
    59
    Thanks
    0
    Thanked 16 Times in 9 Posts
    All the parts for a static cost from Amazon is around $35.00 for 5HP FYI you need a potential relay I like APR5 works the best
    Now if find a old use 3 phase motor star wound now you have rotary converter
    You can add oil run cap make look better but that all

    Dave






    Quote Originally Posted by old kodger View Post
    Hi Dave,
    These are precisely the considerations that have stopped me proceeding with experiments in that area to date.
    I have seen commercial converters and I think that they use a lead and lag circuit based on inductors for one side and capacitors for the other leaving a primary circuit in the middle as the center phase, but they're very expensive.
    Regards,
    Rob.
    Attached Thumbnails Attached Thumbnails Rotary Phase Converter (Create 3-phase power from a single phase source)-three-phase.jpg  
    Last edited by smithdoor; Jan 14, 2017 at 04:30 PM.

  10. #9
    Supporting Member
    Join Date
    Oct 2016
    Posts
    1,113
    Thanks
    25
    Thanked 423 Times in 296 Posts

    old kodger's Tools
    Hi Dave,
    I quite readily concede to not being an expert in anything, so, when I say that all of the info on potential relays that I have managed to locate on the net, seem to refer to "split phase" power supplies I can comprehend how the relay works. However, I'm in Australia and our 230 volt supply is ONE HOT LINE AND ONE EARTH BOUND NEUTRAL. there is ,L1 or L1 or L1, there is NO L2, so unless I'm missing something fundamental here (if so, I hope you will explain), I cannot see how a potential relay is going to help.
    Regards,
    Rob.

  11. #10
    Supporting Member smithdoor's Avatar
    Join Date
    Feb 2016
    Location
    Clovis CA
    Posts
    59
    Thanks
    0
    Thanked 16 Times in 9 Posts
    The relay turns the start cap off after the motor starts
    The potential relay APR5 is adjustable for voltages (130-370Volts)
    You find this type of relay use in AC and deep well water pumps
    I replace centrifugal switch found in single phase motors
    The first drawing below shows a typical single phase motor use a potential relay
    Note the start winding is 90° to then main winding this give the motor the direction to turn
    For three phase the winding are at 120° The second drawing shown how it is wired for three phase

    Dave





    Quote Originally Posted by old kodger View Post
    Hi Dave,
    I quite readily concede to not being an expert in anything, so, when I say that all of the info on potential relays that I have managed to locate on the net, seem to refer to "split phase" power supplies I can comprehend how the relay works. However, I'm in Australia and our 230 volt supply is ONE HOT LINE AND ONE EARTH BOUND NEUTRAL. there is ,L1 or L1 or L1, there is NO L2, so unless I'm missing something fundamental here (if so, I hope you will explain), I cannot see how a potential relay is going to help.
    Regards,
    Rob.
    Attached Thumbnails Attached Thumbnails Rotary Phase Converter (Create 3-phase power from a single phase source)-single-phase-model-1-.jpg   Rotary Phase Converter (Create 3-phase power from a single phase source)-2three-phase.jpg  
    Last edited by smithdoor; Jan 15, 2017 at 06:21 AM.

Thread Information

Users Browsing this Thread

There are currently 3 users browsing this thread. (0 members and 3 guests)

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •